Requirements
- U60 Echelon device
- Install Echelon NodeUtils software
Setting up U60 Echelon device
- Connect U60 to the USB port of your computer
- The left LED should blink orange once
LonWorks Interface
- Open LonWorks Interface in control panel
Test your connection
- Select your LON interface
- Click “Test” icon ⇒ Network interface node Status must appear
Service pin test
- Click Comm to allow to receive a service pin message from the desired neuron ID
- Press Service pin button of the equipment
- The green LED of the U60 should blink green when pressing it
- The below message must appear every time the button is pressed
- The green LED of the U60 should blink green when pressing it
==> If these messages are displayed, the communication with the device is deemed good